We use the trussed tower design methods. The lattice framework is appropriate for single sided frames, not multiple frames. The trussed towers accounts for member shielding on the back side. Back some years ago we were always debating this in the office (and with some other consultants). Some people would use trussed towers, some would use the lattice frameworks. I found some information on the matter in "Wind Loads on Petrochemical & Other Facilities" and then further information leading all the way back to the ANSI A58 document (with references). The petrochemical document takes the research and consolidates it into a useful design method. The nuts and bolts of it are that you can more or less use the towers information and while not exact it will be pretty close depending on how your frames are built. (I think the towers information assumes a 1:1 aspect ratio for shielding which may or may not be true). You can conservatively (very conservatively) use lattice frameworks, but if you do you should apply the 1.6, 1.8, 2.0 to both leeward and windward frames independently in full non reduced load.