southard2
Structural
- Jul 25, 2006
- 169
Note 6 in ASCE 7-02 Figure 6-10 states, " Except for moment resisting frames, the total horizontal shear shall not be less than that determined by neglecting wind forces on roof surfaces.
The question is what does it mean by roof surfaces For 3:12 and 4:12 roof slopes the net horizontal forces of roof zones 2 and 3 will be negative while the net horizontal force on the walls is positive.
I've always interpreted note 6 to mean that when figuring the loading on my diaphragm I am to totally neglect the roof forces (make them zero) when they are net negative. In truth I usually flip the negative sign to a positive to be safe cause I've never felt comfortable with just making them zero.
I've had an engineering crisis of faith so I started researching. The wind load calc guide is vague just like ASCE 7-98 and ASCE 7-02. In fact ASCE 7-02 is more clear. Still I'm not sure. So I compare some wind loads using the different methods. When I use the all heights method the roof forces turn positive in some of the load cases always (usually anyway) resulting in a higher diaphragm load than the anaylitical less than 60 ft method. However when I used the simplified method less than 60ft (here ASCE states very clearly to zero out the negative loads) I got pretty much the same results as the less than 60ft analytical method.
1) So is my interpretation right?
2) If so why is the all heights method the only method that has load cases where Cp on the windward roof is not negative (remember I'm talking about low slope roofs)?
3) If I'm wrong should I just ignore the windward roof loads or what?
Any help would be appreciated
The question is what does it mean by roof surfaces For 3:12 and 4:12 roof slopes the net horizontal forces of roof zones 2 and 3 will be negative while the net horizontal force on the walls is positive.
I've always interpreted note 6 to mean that when figuring the loading on my diaphragm I am to totally neglect the roof forces (make them zero) when they are net negative. In truth I usually flip the negative sign to a positive to be safe cause I've never felt comfortable with just making them zero.
I've had an engineering crisis of faith so I started researching. The wind load calc guide is vague just like ASCE 7-98 and ASCE 7-02. In fact ASCE 7-02 is more clear. Still I'm not sure. So I compare some wind loads using the different methods. When I use the all heights method the roof forces turn positive in some of the load cases always (usually anyway) resulting in a higher diaphragm load than the anaylitical less than 60 ft method. However when I used the simplified method less than 60ft (here ASCE states very clearly to zero out the negative loads) I got pretty much the same results as the less than 60ft analytical method.
1) So is my interpretation right?
2) If so why is the all heights method the only method that has load cases where Cp on the windward roof is not negative (remember I'm talking about low slope roofs)?
3) If I'm wrong should I just ignore the windward roof loads or what?
Any help would be appreciated