Structural
- Mar 8, 2012
- 21
Hello,
I am designing a 5 story wood framed hotel building approx 53' x 180' footprint. I am ending up with large pressures to design my plywood shearwalls for, and no difference in pressure between interior and corner zones. Is this correct?
Here are some details about the project:
I am using ASCE7-05, category II building, Exposure C, 130 mph, h = 65 feet
So because this building is over 60 feet tall, I am using the general MWFRS equation in ACCE7-05 6.5.12.2.1
I am ending up with 63 psf acting at the top of the building down to 55 psf acting at the bottom of the building.
I am used to using the lambda value and Figure 6-2 that has much lower interior zone pressure values.
From figure 6-2 for a low-rise 60 foot tall building, the pressure would be 60 psf at the corner zones and 40 psf at the interior zones.
Is it correct that there is no reduced pressure at interior zones on non-lowrise buildings?
Thank you for your time!
--Luke
I am designing a 5 story wood framed hotel building approx 53' x 180' footprint. I am ending up with large pressures to design my plywood shearwalls for, and no difference in pressure between interior and corner zones. Is this correct?
Here are some details about the project:
I am using ASCE7-05, category II building, Exposure C, 130 mph, h = 65 feet
So because this building is over 60 feet tall, I am using the general MWFRS equation in ACCE7-05 6.5.12.2.1
I am ending up with 63 psf acting at the top of the building down to 55 psf acting at the bottom of the building.
I am used to using the lambda value and Figure 6-2 that has much lower interior zone pressure values.
From figure 6-2 for a low-rise 60 foot tall building, the pressure would be 60 psf at the corner zones and 40 psf at the interior zones.
Is it correct that there is no reduced pressure at interior zones on non-lowrise buildings?
Thank you for your time!
--Luke