vato
Structural
- Aug 10, 2007
- 133
Table 4.2a and 4.3a require a 50% reduction in capacity for ASD loads.
asce 7-10 reduces wind load by a factor of .6 in all ASD load combinations.
So, when I design a shear wall or diaphragm, do I:
1. determine load from ASCE 7-10
2. reduce load by .6 to reflect ASD load combo
3. then use half capacity from t4.2a and 4.3a
OR is the 50% reduction for ASD actually reflect the 0.6 factor on my ASD load combos.
Also, should I use a .6 wind load to figure tension and compression on a shear wall
before choosing simpson tiedowns?
I probably shouldn't be confused by this, but lack of sleep is not helping at the moment.
Thanks in advance for the clarification.
asce 7-10 reduces wind load by a factor of .6 in all ASD load combinations.
So, when I design a shear wall or diaphragm, do I:
1. determine load from ASCE 7-10
2. reduce load by .6 to reflect ASD load combo
3. then use half capacity from t4.2a and 4.3a
OR is the 50% reduction for ASD actually reflect the 0.6 factor on my ASD load combos.
Also, should I use a .6 wind load to figure tension and compression on a shear wall
before choosing simpson tiedowns?
I probably shouldn't be confused by this, but lack of sleep is not helping at the moment.
Thanks in advance for the clarification.