- 21
I have heard from so many sources that the ventilation requirements for a building no matter what it is should be 15 CFM per person. However, I thought that that is what the ASHRAE 62 (1989) requirement says. Now we have the ASHRAE 62 (2010) requirement which says that for places of religious worship there needs to be 5 CFM per person and 0.06 CFM per square foot. If that is the case the ventilation rate in every zone is at least halved. My questions are the following.
1) Is the ventilation rate for places of religious worship 5 CFM per person plus 0.06 CFM per square foot per ASHRAE 62 (2010)? Example A room with a maximum occupancy of 230 people and 2800 square feet would be (230 people)*(5 CFM per person)+(2800 square feet)(0.06 CFM per square foot)= 1318 CFM
or is it 15 CFM per person which would give me the results of 3450 CFM
2) Also, is there other methods for reducing the ventilation air requirement? (i.e. air ionizers in the air handling unit or other means)?
Thanks for your help
1) Is the ventilation rate for places of religious worship 5 CFM per person plus 0.06 CFM per square foot per ASHRAE 62 (2010)? Example A room with a maximum occupancy of 230 people and 2800 square feet would be (230 people)*(5 CFM per person)+(2800 square feet)(0.06 CFM per square foot)= 1318 CFM
or is it 15 CFM per person which would give me the results of 3450 CFM
2) Also, is there other methods for reducing the ventilation air requirement? (i.e. air ionizers in the air handling unit or other means)?
Thanks for your help