DanCP93
Mechanical
- Apr 17, 2003
- 2
Does anyone the most effective design to meet the Fan Power Limiation as listed in the ASHRAE Energy Efficiency Standard 90.1 for large commerical buildings?? Larger Ductwork, Lower Coil Velocities, Smaller, but more AHUs.....
Const Vol Sys Var Vol Sys
<20000 cfm 1.2hp/1000cfm 1.7hp/1000cfm
>20000 cfm 1.1hp/1000cfm 1.54hp/1000cfm
Const Vol Sys Var Vol Sys
<20000 cfm 1.2hp/1000cfm 1.7hp/1000cfm
>20000 cfm 1.1hp/1000cfm 1.54hp/1000cfm