cex10k
New member
- Nov 20, 2017
- 11
Dears,
I have sized a piping according to formulas of chapter IX "High pressure piping" (K304.1.2), the internal design gage pressure is 315 bar. Could I set the pressure relief valve at 330 bar (+4.7%)?
According to paragraph K322.6.3(b) I could. Or have I misinterpreted the text?
Thanks
Regards
Michele
I have sized a piping according to formulas of chapter IX "High pressure piping" (K304.1.2), the internal design gage pressure is 315 bar. Could I set the pressure relief valve at 330 bar (+4.7%)?
According to paragraph K322.6.3(b) I could. Or have I misinterpreted the text?
(b) System protection must include one relief device
set at or below the design pressure at the operating
temperature for the relieving condition, with no device
set to operate at a pressure greater than 105% of the
design pressure, except as provided in (c) below.
Thanks
Regards
Michele