breadboard
Electrical
- May 27, 2012
- 11
In the Aspen Breaker Rating module there is an example for breaker and a half configurations (Section 3.3.3 in the instructions) where it states for the breakers attached to one of the buses they consider the possibility that the breaker might have to interrupt the total bus current. I don't see other than the case for a 2 bay breaker and a half and one bus breaker fails why this would be the case. Does anyone know the logic why they would be using the total bus fault current? Seems to me that would make your breakers come out underrated.