This may seem like a repeat thread, but I have some questions.
I have a large room in a smoke exhaust condition. There is mechanical exhaust and mechanical makeup, and, by design, a flow differential between the two.
I am being asked to provide the differential pressure between the room and atmosphere, to assist in calculations for door weight during egress.
I have the equation for door opening forces from ASHRAE Applicaitons, 52.6: F=Fdc+((5.20*W*A*deltaP)/2(W-d))
I have all the other variables but need the differential.
I note that user "quark" quoted this:
"The pressure of the room is [cfm(in)-cfm(exh.)]/room volume*101327. The pressure terms are in Pascals."
I have a cfm balance of -36,000cfm and a room volume of 84,285 cu. ft.
This gives me a differential pressure in pascals of 4.21E-6, or 1.69x10^-8 inches water gage...I have issues believing this!
This is an approximation so I am happy to disregard leakage in this case.
Can anyone point me at a pressure assessment calc for the room? Thanks in advance.
I have a large room in a smoke exhaust condition. There is mechanical exhaust and mechanical makeup, and, by design, a flow differential between the two.
I am being asked to provide the differential pressure between the room and atmosphere, to assist in calculations for door weight during egress.
I have the equation for door opening forces from ASHRAE Applicaitons, 52.6: F=Fdc+((5.20*W*A*deltaP)/2(W-d))
I have all the other variables but need the differential.
I note that user "quark" quoted this:
"The pressure of the room is [cfm(in)-cfm(exh.)]/room volume*101327. The pressure terms are in Pascals."
I have a cfm balance of -36,000cfm and a room volume of 84,285 cu. ft.
This gives me a differential pressure in pascals of 4.21E-6, or 1.69x10^-8 inches water gage...I have issues believing this!
This is an approximation so I am happy to disregard leakage in this case.
Can anyone point me at a pressure assessment calc for the room? Thanks in advance.