Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Assistance in sizing XFMR 1

Status
Not open for further replies.

jnix1

Electrical
Oct 6, 2010
1
0
0
US
I have attached a sheet detailing the load on a given unit. Note that there will be two (2) of these units. In addition, there will be some six (6) 400W flood lights, a PLC, a window unit AC, a couple of 100A distribution panels, etc.

Everything is 480V or less.

I was hoping someone could tell me an appropriate sive (kVA) for the transformer.

Furthermore, any "rule of thumb"...i.e. some "X" number of kVA for "Y" number of Amps, Watts, etc. would be appreciated.
 
Replies continue below

Recommended for you

The "Running Mode KVA Eq" looks like a good estimate of running load. Two of these equals 2 x 133 kva = 266 kva. All of the other misc load will run around 20 kva. A 300 kva 3-phase transformer would handle the running load, but I would chose a 500 kva transformer to handle the running load with ease, and also handle the 125 hp motor startups.
500 kva 277y/480
 