Attic Eaves and Hips

Status
Not open for further replies.
Sep 16, 2016
30
Question on attic layouts, superficially hips. In an effort to design a better attic we've started looking into placing heads directly under the hips. The picture attached is a quick sketch on top of 8.6.4.1.4.3 on 2016e NFPA 13. If we are trying to stay under 8' against the slope between heads, on one side of a hip our coverage per head would 4' x 7'6" max, but then on the other side of the hip it would be reversed, creating an uneven coverage area. I feel like I'm missing some easy to understand thing here, but any advice would be helpful.

Attic_snylmm.jpg
 
Replies continue below

Recommended for you

Are you using Tyco attic sprinklers?
 
It looks like you would have more than enough coverage there. Standard sprinklers need only be 6 ft. apart, not 8 ft.
 