n8engr
Structural
- Mar 2, 2001
- 22
I am running into some problems with a project involving auger cast piles. This involves a new pipe rack we have designed that will be placed within an existing refinery. There are many places that have either existing foundations nearby or existing piping running about 1'-0" above grade.
The geotech report called for piles to be used so we had no choice in that matter. We decided to go with auger cast piles with the thinking this would be the best option for installation with existing objects nearby.
The contractor has expressed concern with being able to install these piles as he wants a 4'-0" diameter safety cage around the auger during installation (piles are 12" dia.). This cage goes into the ground approximately 1'-0". This obviously will not work due to nearby interferences. My question for you all is...is this typical for ACP installation? Do you know of any alternatives I could offer to work around existing foundations etc.? See attachment for details. Thanks...
The geotech report called for piles to be used so we had no choice in that matter. We decided to go with auger cast piles with the thinking this would be the best option for installation with existing objects nearby.
The contractor has expressed concern with being able to install these piles as he wants a 4'-0" diameter safety cage around the auger during installation (piles are 12" dia.). This cage goes into the ground approximately 1'-0". This obviously will not work due to nearby interferences. My question for you all is...is this typical for ACP installation? Do you know of any alternatives I could offer to work around existing foundations etc.? See attachment for details. Thanks...