ThStructuresGuy
Structural
- Nov 14, 2017
- 7
I have a project with 16" diameter auger cast piles and a cage with 7-#8 bars with #3 ties. We have specified a 3" clear for the cage, however some of the pile cages have come up with a 1 3/4" cover (project is under construction). To me this is out of specification per ACI 117 2.2.2 "-1/2 when member is over 12in" and/or ACI 318 7.5.2.1.
Are there any code requirements where we can reduce the required cover to less than 3"? Two of the piles out of tolerance are gravity only, the third is at a P5 lateral pile cap.
Is the solution to abandon the pile and construct a new one, I can't think of another repair solution.
Are there any code requirements where we can reduce the required cover to less than 3"? Two of the piles out of tolerance are gravity only, the third is at a P5 lateral pile cap.
Is the solution to abandon the pile and construct a new one, I can't think of another repair solution.