arbil
Electrical
- Nov 2, 2008
- 17
We are having a 6.6 KV,1500 KW motor with auto transformer starting .The tap setting of auto transformer is at 60% .As per the motor data sheet/curves,at 60% tap, the motor starting time is 11 seconds and thermal withstand time is 17 seconds.
As per the control scheme , the changeover from auto transformer start to normal operation is dependent on timer 't1','t2' and current relay , i.e the set minimum time 't1'(set at 6 sec) should elapse AND starting curent should come down.If current does not fall within time 't2' , the main circuit breaker will trip.
The timer setting 't2' is kept at 15 sec , i.e. 2 sec less than the thermal withstand time .
Now the problem is that we are not able to run the motor as the starting surrent is not coming down within 15 seconds .Normally this would have indicated problem with the pump or discharge valve .However both have been checked and no problem has been observed .Bearing conditions are also OK .We cannot increase the timer 't2' setting also , as it will cross the thermal withstand time .Motor starting is OK in decoupled condition .System voltage is also stable .We are not able to ascertain where the actual problem is .
Is there any other method or site test by which we can diagnose the actual problem ?
As per the control scheme , the changeover from auto transformer start to normal operation is dependent on timer 't1','t2' and current relay , i.e the set minimum time 't1'(set at 6 sec) should elapse AND starting curent should come down.If current does not fall within time 't2' , the main circuit breaker will trip.
The timer setting 't2' is kept at 15 sec , i.e. 2 sec less than the thermal withstand time .
Now the problem is that we are not able to run the motor as the starting surrent is not coming down within 15 seconds .Normally this would have indicated problem with the pump or discharge valve .However both have been checked and no problem has been observed .Bearing conditions are also OK .We cannot increase the timer 't2' setting also , as it will cross the thermal withstand time .Motor starting is OK in decoupled condition .System voltage is also stable .We are not able to ascertain where the actual problem is .
Is there any other method or site test by which we can diagnose the actual problem ?