jhonsom
Electrical
- Nov 13, 2009
- 32
We tried Autosync of an old diesel start gas plant with settings like 0.5 Hz/s characteristics, 0.25s pulse, 10s pulse interval for frequency control and it worked ok.
How different is a hydro plant in terms of settings? Could I use the same settings? We couldn't obtain the characteristics from both the plants as it is pretty old.
Also does autosynchronization require supervision like contact close or is ok to close the breaker automatically without supervision once Autosync is started , which of these is normally used in the field?
How different is a hydro plant in terms of settings? Could I use the same settings? We couldn't obtain the characteristics from both the plants as it is pretty old.
Also does autosynchronization require supervision like contact close or is ok to close the breaker automatically without supervision once Autosync is started , which of these is normally used in the field?