basicbill

Electrical
Jun 2, 2011
3
Hi all...first post.
I am a journeyman electrician and I teach electrical apprentices. I have a question on how to calculate auto-transformer secondary fault currents.
I don't require engineering level calculations...just the concepts behind the calculation.

As I understand it an auto-transformer will 'transform' only a portion of the required secondary current and the rest is supplied directly from the primary line. Of course, there is no electrical isolation primary/secondary.

With this in mind, are secondary 'bolted fault' calculations able to be performed using the auto-transformer's kVA and %Z or rather should it be calculated using the previous transformer kVA rating and %Z? I realize that there is a choking effect of the series portion of the auto-transformer, line impedences etc.

But my main question is....would you use the ratings of the auto-transformer or the upstream isolating coil type transformer to perform fault current calculation.

I hope I have stated my question clearly.

Thanks in advance.
 
Replies continue below

Recommended for you

You really need to account for both. For fault calculations you can ignore the "auto" and just focus on the "transformer" part. Size(rating) and %Z are what you need.
 
@basicbill: Can you please explain what is a bolted fault?
 
Correct....thanks David.

So to re-state my question....

Do I have to consider the VA rating of the upstream transformer that supplies the auto-transformer when doing the fault current calculation? Since there is a direct electrical connection to it; as well as to the auto-transformer.
 
As well as the %Z of the upstream transformer.
 
Hi BasicBill: The answer is " it depends how accurate an answer you want". I'll do an example : a Utility feeds a transfo (T1) rated 1000kva/ 480v-3ph secondary and z=5%. Assume the utility is infinite (an approximation). The 3ph fault at secondary of T1 is 1000kva/(.48kv*1.732*.05)=24ka .
This T1 feeds autotransfo T2,rated 225kva/440v-3ph sec and z=5%. ( another approx is to assume negligible z for the cable between T1 and T2)
a) if we ignore the upstream T1, then the 3ph fault on the sec of T2 (440v) = 225kva/(.44kv*1.732*.05)= 5.9ka .

b) if we include the effect of T1,we have to convert T1's impedance on T2's base and then add it to T2's z; so, this is done as follows : 24ka*.48kv*1.732 = 20mva ; .225mva/20mva = 0.01125 = 1.125% ( T1's equivalent z, as seen by T2 ); then the 3ph fault on the sec of T2 (440v) = 225kva/ (.44kv*1.732*.06125)= 4.82ka .
I hope this helps. ( another approximation was ignoring resistance component of z ). Ovide.
 