In the case of bulk power transfer, why is the autotransformer between the two lines grounded WYE: grounded WYE? ie 500KV:230KV or 230Kv:69KV
 
Replies continue below

Recommended for you

Wye not? It provides a defined phase to ground voltage and nice clean connections; try to draw out the connection diagram for a delta-delta autotransformer.
 
Usually to avoid a phase shift. Delta connected autotransformers cause a phase shift.
respectfully
 
The earthy end of the winding can be insulated to a lower voltage than the line end in a star connected design is used. A delta connection requires the full winding to be insulated for line voltage. At very high voltages the insulation takes up a signficant amount of the core window so the saving can be significant.


----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
Try drawing a Delta-Wye autotransformer.
 
Good one! BJC!

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
I had considered saying something about wye-delta autotransformers but the concept was so outlandish I didn't bother. You could do an open delta autotransformer using two single-phase autotransformers but there just isn't a way to close it.
 