I would like to tap into our motor experts.
I am working on an internal study to improve the ride-through capability of VFDs. This led me to deal with several low voltage induction motors that are part of larger motor’s auxiliary system interlocking system. Cut the story short, I would need to get some interlocked auxiliary process system motors’ contactor circuits not to drop-off on a transient undervoltage less than 85% (say 70% or less). The solution is to connect the contactor circuit from a UPS power. In this regard during a equal or less than 70% voltage dip caused by utility disturbances,
Now these low voltage motors (0.5 to 3 HP) are seal pump and cooler motors for the larger motor’s sealing system in which certain circulating pressure needs to be maintained and hence a certain amount of motor torque and consequent flow rate/pressure needs to be maintained so as not to contaminate the larger pump’s seal (the suction pressure needs to be lower than the seal pressure). WE are planning to consider an auto-restart in 2 seconds at the larger VFD driven main motor. This means, the smaller LV motors will be subjected to 2 seconds voltage dip of less than 85%. If the main motor auto-restart timer lapse and voltage does not recover to > 70%, the VFD protection will terminate the gating process, shutdown the VFD. The auxiliary system LV motors may still be running on a circulating mode.
My questions are universal to all TEFC induction motor between 0.5~3 HP:
I am working on an internal study to improve the ride-through capability of VFDs. This led me to deal with several low voltage induction motors that are part of larger motor’s auxiliary system interlocking system. Cut the story short, I would need to get some interlocked auxiliary process system motors’ contactor circuits not to drop-off on a transient undervoltage less than 85% (say 70% or less). The solution is to connect the contactor circuit from a UPS power. In this regard during a equal or less than 70% voltage dip caused by utility disturbances,
Now these low voltage motors (0.5 to 3 HP) are seal pump and cooler motors for the larger motor’s sealing system in which certain circulating pressure needs to be maintained and hence a certain amount of motor torque and consequent flow rate/pressure needs to be maintained so as not to contaminate the larger pump’s seal (the suction pressure needs to be lower than the seal pressure). WE are planning to consider an auto-restart in 2 seconds at the larger VFD driven main motor. This means, the smaller LV motors will be subjected to 2 seconds voltage dip of less than 85%. If the main motor auto-restart timer lapse and voltage does not recover to > 70%, the VFD protection will terminate the gating process, shutdown the VFD. The auxiliary system LV motors may still be running on a circulating mode.
My questions are universal to all TEFC induction motor between 0.5~3 HP:
- If UPS is applied to the contactor circuit feeding these motors, the contactor can be held closed during a transient voltage dip of 70% or less. In this regard, the running motor will be subjected to the same amount of undervoltage. In this regard, the speed may not change but the motor torque will weaken, and the torque curve can shift downwards and/or to the left. With the amount of load torque requirement at the shaft, the speed may decrease. Is my assumption correct?
- If item “a” is true. Is the amount of decrease in speed owing to the weakening of motor torque be large enough to cause the speed to significantly decrease and place the seal system in jeopardy? The motors are normally 80% loaded by design.
- If the VFD auto restart delay is only 2 seconds and will shut down if the voltage does not recover after 2 seconds, will this be a big of a deal with the seal pump motor if we will create an interlock to trip the seal motors when the main motor is tripped or place an undervoltage voltage device with a 5 second time delay?