Sir,
We have a substation where 110kv is stepped down to 11kv via a 10MVA ynyn transformer . Three 11kv feeders are used for ditribution. The 11kv and 110kv side nuetrals are solidly grounded . The substation auxiliary supply is maintained through an 11/0.44kv Dyn transformer of which the neutral in the 0.44kv side has been solidly grounded.
We experienced that the 0.44kv side fuses are blowing off for a particular feeder ground fault. We found that this is not happening for faults of other feeders. We checked the ground resistance of transformer neutrals and found ok. The 0.44kv lines and 11kv cables are seperately routed and we think no chances of induction.
Finally , we noticed only one thing. The particular 11kv feeder was feeding to one direction and other feeders are feeding lines to the other direction. The auxiliary transformer is situated in the same direction of the particular feeder.
Let us analyse in this way. For an earthfault in the particular feeder the fault current will flow through ground from the fault point to the transformer 11kv side neutral. As the auxiliary transformer is situated between the fault point and 11kv side neutral of the 110/11kv transformer, the potential of 0.44kv side neutral increased which led to blowing of fuses. Please note that the 11kv side of the auxiliary transformer is delta connected.
Is my analysis correct? If not, what may be the possibilities? What checks I have to conduct further? I expect your valuable comments.
With regards,
appunni
We have a substation where 110kv is stepped down to 11kv via a 10MVA ynyn transformer . Three 11kv feeders are used for ditribution. The 11kv and 110kv side nuetrals are solidly grounded . The substation auxiliary supply is maintained through an 11/0.44kv Dyn transformer of which the neutral in the 0.44kv side has been solidly grounded.
We experienced that the 0.44kv side fuses are blowing off for a particular feeder ground fault. We found that this is not happening for faults of other feeders. We checked the ground resistance of transformer neutrals and found ok. The 0.44kv lines and 11kv cables are seperately routed and we think no chances of induction.
Finally , we noticed only one thing. The particular 11kv feeder was feeding to one direction and other feeders are feeding lines to the other direction. The auxiliary transformer is situated in the same direction of the particular feeder.
Let us analyse in this way. For an earthfault in the particular feeder the fault current will flow through ground from the fault point to the transformer 11kv side neutral. As the auxiliary transformer is situated between the fault point and 11kv side neutral of the 110/11kv transformer, the potential of 0.44kv side neutral increased which led to blowing of fuses. Please note that the 11kv side of the auxiliary transformer is delta connected.
Is my analysis correct? If not, what may be the possibilities? What checks I have to conduct further? I expect your valuable comments.
With regards,
appunni