Auxiliary Tripping Relay: Use of parts with reduced coil DC ratings for faster operation. Typical Circuit Doubt.

Distribution73

Electrical
Mar 18, 2015
41
Hello,
While reviewing drawings from an (old) existing substation, I have come across a number of tripping circuits where auxiliary relays (normally GE HFA51A type) are used in an arrangement I cannot quite understand.
These auxiliary relays are used in Busbar Diff and CBF circuits, where contacts of protection relays energize these auxiliary relays coils. The substation DC is 125Vdc, but the auxiliary tripping relay coils are 12Vdc rated. I understand this is something actually recommended by the aux relay manufacturer to increase speed of operation of the aux relay. What I dont understand is the use made of a resistor is series with the aux relay coils. I attach a circuit sample. I have seen IEEE recommendations (https://www.pes-psrc.org/kb/report/017.pdf) and this type of series resistor appears shunted by a NC contact of the auxiliary relay or a capacitor. I understand this being intended to allow full 125VDC excitation of the aux relay coil during a few milliseconds and then protect the coil once the aux relay has operated. In the substation however the resistor is permanently in series with the coil. Any feedback on the rationale of such arrangement (with a resistor permanently in series) would be greatly appreciated. It appears to me to be defeating the purpose of using a reduced DC rating coil.

On a similar note I have seen the coils been protected with diodes in parallel. These have resistor in series. Any feedback/source where I could learn what are the basis for the dimensioning of these parallel resistances would also be much appreciated.
Thank you in advance for the help.
 

Attachments

  • Captura.JPG
    Captura.JPG
    107.1 KB · Views: 4
Replies continue below

Recommended for you

Hello,
While reviewing drawings from an (old) existing substation, I have come across a number of tripping circuits where auxiliary relays (normally GE HFA51A type) are used in an arrangement I cannot quite understand.
These auxiliary relays are used in Busbar Diff and CBF circuits, where contacts of protection relays energize these auxiliary relays coils. The substation DC is 125Vdc, but the auxiliary tripping relay coils are 12Vdc rated. I understand this is something actually recommended by the aux relay manufacturer to increase speed of operation of the aux relay. What I dont understand is the use made of a resistor is series with the aux relay coils. I attach a circuit sample. I have seen IEEE recommendations (https://www.pes-psrc.org/kb/report/017.pdf) and this type of series resistor appears shunted by a NC contact of the auxiliary relay or a capacitor. I understand this being intended to allow full 125VDC excitation of the aux relay coil during a few milliseconds and then protect the coil once the aux relay has operated. In the substation however the resistor is permanently in series with the coil. Any feedback on the rationale of such arrangement (with a resistor permanently in series) would be greatly appreciated. It appears to me to be defeating the purpose of using a reduced DC rating coil.

On a similar note I have seen the coils been protected with diodes in parallel. These have resistor in series. Any feedback/source where I could learn what are the basis for the dimensioning of these parallel resistances would also be much appreciated.
Thank you in advance for the help.
Hey!

What you're describing makes sense — using a lower voltage coil with a series resistor on a higher DC voltage can speed up relay operation while limiting current afterward. Even if the resistor is always in series (not just during pickup), it still limits the steady-state current, preventing coil damage. Maybe the design prioritizes faster operation with some current limiting, without the added complexity of a bypass circuit.

As for the diode with a series resistor, that’s usually for coil transient suppression (like a flyback diode). The resistor slows the diode response a bit, reducing the relay's dropout time. Sizing depends on coil inductance and desired suppression level — IEEE and relay manufacturer docs are great for guidelines.

Let me know if you want to dig into the math!
 