So it happened again today when I gave an engineer an estimate of fault current at the terminals of a 120/240 V single phase transformer. He was agast. Dealt with lots of other utilities, and never heard of a 75kVA that could deliver so much current. First he had a hard time believing that half winding line to ground faults deliver about 1.5 X the full winding line to line value. He's going to check with some manufacturers on this point.
I assume infinite bus on the primary. I use a low limit impedance from our specs, not the nameplate, since transformer may be replaced at some point. I lower that value by a factor of 7.5% based on ANSI/IEEE impedance tolerances. Voltage is increased 5% also based on standards.
What's going on? Am I overly conservative? Why aren't others giving similar figures? On what basis are they ignoring the line to ground (most common type of fault)multiplier. What do you do?
I assume infinite bus on the primary. I use a low limit impedance from our specs, not the nameplate, since transformer may be replaced at some point. I lower that value by a factor of 7.5% based on ANSI/IEEE impedance tolerances. Voltage is increased 5% also based on standards.
What's going on? Am I overly conservative? Why aren't others giving similar figures? On what basis are they ignoring the line to ground (most common type of fault)multiplier. What do you do?