Avg. BTU Rating for Appliances (Microwaves, Refrigerators, Etc.)

Status
Not open for further replies.

supaman79

Mechanical
Jul 26, 2004
56
Does anyone know where I can find an avg. BTU rating for refrigerators to apply to my cooling loads? I've looked in the ASHRAE handbooks, but I can't seem to find anything.
 
Replies continue below

Recommended for you

ASHARE Fundamentals, chapter 29 suggests 300 BTU/hr sensible per 10 ft^3 of interior volume (for small commercial equipment).
 
the sizes and ratings are so varied, I have given up trying to guesstimate one. The fridge duties (compressor ratings) dont help because the motor may only run for a fraction ofthe hour.

I could only estimate the gain by determining the physical external area, then use a typical internal-external temp difference multiplied by the thermal transmittance value.

It wouldn't be much I guess, perhaps 20W/m2 of fridge area for internal at -20 c and room at 20C.

so for fridge at 2m high x 0.6x0.6 (we have small fridges in the UK) then =96Watts (excludes allowance for compressor COP etc) I would allow something like 150Watts to be on the safe side.


Friar Tuck of Sherwood
 
Thanks guys,

You were a big help. Friartuck is there anything you don't know? haha
 
Not sure if you know the power consumption, but if you did couldn't you convert the watts of power input directly to BTUH?
 