I think this question is special for Mr.Catserveng, as he is a super specialist for this AVR model, as I notice.
We had situation long time ago, with two same size genset running, equipped DECS200. After few days of stable running, VARs from one generator moved to another, and we got 0.9MW/0.6MVAR and 0.9MW/0.01MVAR. It was continuosly running without trip, until we had to stop them for service. Temperatures of windings were OK, AVR also did not show any alarm.
Our electrical engineer said that it is not problem since KW is sharing, so we forgot about it. But after that several times we noticed same scenario.
Is it really OK?
We used DEIF parallel controller for sync. Decs in AVR mode (AUTO). Voltage matching OFF.
Later I found suggested setting list from comissioning engineer, where AVR is STOP, voltage matching is ON. I read manuals, but did not get point for VAR walking. Could that two settings make sence for that?
Viktor
Electrical Technician II
We had situation long time ago, with two same size genset running, equipped DECS200. After few days of stable running, VARs from one generator moved to another, and we got 0.9MW/0.6MVAR and 0.9MW/0.01MVAR. It was continuosly running without trip, until we had to stop them for service. Temperatures of windings were OK, AVR also did not show any alarm.
Our electrical engineer said that it is not problem since KW is sharing, so we forgot about it. But after that several times we noticed same scenario.
Is it really OK?
We used DEIF parallel controller for sync. Decs in AVR mode (AUTO). Voltage matching OFF.
Later I found suggested setting list from comissioning engineer, where AVR is STOP, voltage matching is ON. I read manuals, but did not get point for VAR walking. Could that two settings make sence for that?
Viktor
Electrical Technician II