Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

B16.5 Testing of Insulating flange for Jetty operation

Status
Not open for further replies.

mafla jones

Mechanical
Jul 31, 2018
14
SG
Hi All, How do you perform a Continuity and discontinuity test on a Insulation flange that transport hydrocarbon?

should we use a “Megger” and what is the required voltage set . Also, I read somewhere in the internet that use of Megger in such test, line should be dried.

Kindly advice please?
Mafla Jones
 
 https://files.engineering.com/getfile.aspx?folder=f7fb0c3b-ff0f-40fe-a667-288a249e86be&file=Insulating_Flange_Testing_Procedure.doc
Replies continue below

Recommended for you

We use an old Avo Model 8 analogue multimeter which has a 15V drive voltage for the higher resistance ranges. A standard digital multimeter uses a lower voltage on the resistance ranges and doesn't give accurate results. If you have a megger with a 50V capability then that might suffice, but a typical 500V megger won't be any use for this measurement. The Avo 8 is discontinued, but there are still plenty on the aftermarket.
 
"Megger" in this case means a meg-ohm meter, not to be confused with a brand name that makes this style and other types of test instruments.
 
The difference between a megger and 'Megger'. [wink]

Is this a British / British-influenced nickname, or do you guys in the States call insulation resistance testers 'meggers' too?
 
We in the USA generically call a megohmmeter a Megger, a DLRO a ductor, power factor testing Doble and soft tissue used to wipe the nose Kleenex ;)
 
Megger or megger in my experience generally implies testing with 50V, 250V, 500V, 1000V or 2500 V applied.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 