Waqalevu
Electrical
- Aug 8, 2014
- 18
Due to the failure of our site standby generator, we have had to install a contingency backup supply on a critical area of our plant. The contingency arrangement comprises two 1250 kVA generators connected in parallel to a 400/690 Volt transformer. The transformer is 690 Volt secondary is connected to our MCC busbars. The hire cost for this equipment is huge, and it is likely that we will require this for many weeks.
There is an alternative, albeit we will be very limited with what we can run. I could connect one of the generators to the secondary of a 11kV/400V, 1250 kVA transformer. I can then run the generator if required, using this transformer as a step up and back feed onto the 11 kV bus. The MCC that requires the contingency power is split in two halves, with two incomers and a bus coupler. The bus coupler is normally open, and each half of the board is supplied from a 11kV/690V, 3000 kVA transformer. So what I'm thinking of doing is using the 11kV/400V, 1250 kVA as a step up, with the generator connected to the 400V secondary. The 11 kV would then supply one of the 3000 kVA transformers, stepping the voltage back down to the required 690 Volts. The other transformer would be switched off. I would then limit what I could run, up to the capacity of the 1250 kVA transformer.
This would save the cost of hire of one generator and the step up transformer and cables.
Appreciate if anyone can see any pitfalls with this arrangement.
There is an alternative, albeit we will be very limited with what we can run. I could connect one of the generators to the secondary of a 11kV/400V, 1250 kVA transformer. I can then run the generator if required, using this transformer as a step up and back feed onto the 11 kV bus. The MCC that requires the contingency power is split in two halves, with two incomers and a bus coupler. The bus coupler is normally open, and each half of the board is supplied from a 11kV/690V, 3000 kVA transformer. So what I'm thinking of doing is using the 11kV/400V, 1250 kVA as a step up, with the generator connected to the 400V secondary. The 11 kV would then supply one of the 3000 kVA transformers, stepping the voltage back down to the required 690 Volts. The other transformer would be switched off. I would then limit what I could run, up to the capacity of the 1250 kVA transformer.
This would save the cost of hire of one generator and the step up transformer and cables.
Appreciate if anyone can see any pitfalls with this arrangement.