zdas04
Mechanical
- Jun 25, 2002
- 10,274
I've got a situation where I'm flowing from an ANSI 300 system (PSV set at 600 psig) into an API 3000 wellhead with a potential build-up pressure of 1200 psig if the well is shut in for a couple of days (it is normally less than 40 psig when flowing). I've come across this situation a couple of times before and the solution we used is described in the attachment. No one trusts check valves for isolation, but this approach allows you to verify that the paired checks hold well enough.
The first time I ever used this we did a HazOp on it and the PSM consultant looked at the design and said "that is a legal spec break". We all took him at his word and went on with our lives. We built it and it worked well. We put it on the schedule to be verified when the PSV was tested, and it passed the test every time.
Now I have a client that is saying "why do you say it is a 'legal spec break', is there a document somewhere that defines legal spec breaks and does it include this?". I looked through my library and can't find any requirements for doing anything in particular at a spec break. Reading through all the threads on eng-tips.com most of the discussion is (of course) going from a high pressure rating to a low pressure rating and that requires some sort of positive block (ESD, manual block valve, etc.). The general Interwebz was equally as unhelpful. Going from high MAWP to low MAWP is not the situation I have here, and I'd rather not put an ESD on this line (the ESD valves that this client uses require a person to pump up a hydraulic pressure to open the valve, and it would be tough to pump up the gas and water inlet ESD's and the gas recycle ESD at the same time and if there is a delay the risk of a trip during start up is too high.
Can anyone point me towards something that defines the range of "legal" spec break technologies or is it down to Engineering Judgement which is what my research this morning hints at?
David Simpson, PE
MuleShoe Engineering
Law is the common force organized to act as an obstacle of injustice Frédéric Bastiat
The first time I ever used this we did a HazOp on it and the PSM consultant looked at the design and said "that is a legal spec break". We all took him at his word and went on with our lives. We built it and it worked well. We put it on the schedule to be verified when the PSV was tested, and it passed the test every time.
Now I have a client that is saying "why do you say it is a 'legal spec break', is there a document somewhere that defines legal spec breaks and does it include this?". I looked through my library and can't find any requirements for doing anything in particular at a spec break. Reading through all the threads on eng-tips.com most of the discussion is (of course) going from a high pressure rating to a low pressure rating and that requires some sort of positive block (ESD, manual block valve, etc.). The general Interwebz was equally as unhelpful. Going from high MAWP to low MAWP is not the situation I have here, and I'd rather not put an ESD on this line (the ESD valves that this client uses require a person to pump up a hydraulic pressure to open the valve, and it would be tough to pump up the gas and water inlet ESD's and the gas recycle ESD at the same time and if there is a delay the risk of a trip during start up is too high.
Can anyone point me towards something that defines the range of "legal" spec break technologies or is it down to Engineering Judgement which is what my research this morning hints at?
David Simpson, PE
MuleShoe Engineering
Law is the common force organized to act as an obstacle of injustice Frédéric Bastiat