Dragonclaw

Electrical
Sep 23, 2003
5
EU
Is there a USA or European standard to be followed in order to prevent an unbalance of current in a building installation?
I have a "lot" of signle phase electrical computer equipment to connect to a 220VAC/240VAC utility supply. Each device consumes 300W of input power and I need to install 500 devices. (150KW). If I install all 500 devices onto one of my signle phase lines, then have I broken any building installation requirements?
 
Replies continue below

Recommended for you

I don't believe you will violate any codes but you will likely violate good design. Assuming the original loads were balanced well it would be a good idea to spread the load around to maintain the balance. Otherwise the result could be an unbalance, causing problems with 3 phase equipment or even single phase equiment for that matter. I am assuming the switchgear, cables, etc.. are sized to handle the additional load but I would certainly verify this. Your additional load could violate some standards (namely the NEC) by adding this load and having too small of wire and/or switchgear. Any unbalance discussions, at least as far as the NEC is concerned, are only recommendations and not mandatory.
 
The wire gauge and switch gear are all rated to handle this level of load. However, I do not know of a permissible level of unbalance. Is there a standard or rule (I've heard of a 10% figure, but am unaware of where this comes from)
 
Good design practice and commen sense are NOT covered by Codes.

Codes only cares for saftey not functionality. Meeting Code is a necessary (statutary) requirement but not a sufficient requirement. For example, a reversed wired motor may meet the Code but will not do the job its supposed to do.

So, use you good judgement. The 10% figure is a well accepted figure, based on sound judgement of people who had the experience before , it is worth something.


 