balancing 3 phase

Status
Not open for further replies.

ILCML

Electrical
Jan 4, 2007
52
If I have 208/230 3phase coming into a control ciruit to run a 3 HP motor, and am pulling a leg to use as a 120v supply (with the neutral) for control circuitry, a) will this unbalance the load to an unacceptable level b) if so how can I "rebalance" it?
 
Replies continue below

Recommended for you

"208/230 V" doesn't exist - I'll assume you're talking about 208/120V. There's no problem having 120 V loads provided you have a neutral conductor back to the transformer. There may be some current imbalance, but it won't be a problem.

If you're talking about something other than 208/120V please clarify.
 
The control circuit will demand such a small load current that it will not cause perceptible unbalance on the three phases.
 
is there a formula or a percentage to use to determine whether additional use of the incoming leg will cause unbalance? If so, what could I do to even it out? My guess would be to use a transformer on 2 of the legs and step it down (although that is what I was trying to avoid to begin with)
 
A common practice is to use a small transformer (50 VA for smaller starters) across two phases to provide control power. On 230 V or 208 V systems 230 v or 208 V starter coils are often used to avoid the transformers. The coil load or the transformer is so small as to be insignificant and may be safely ignored.
respectfully
 
If you have 230 V three-phase, you can have 120 V (115 V) only on one leg of the transformer. So any 120 V load means the system will not be perfectly balanced.

But as long as 120V loads are small fraction of the three-phase loads, the imbalance does not cause any signficant problems.
 
the 120 leg will have a total load nearly that of the motor using teh 3 phase. At what point should I be using a transformer, 50%? 25%? 5%?
 
The transformer will not balance the load. You use a transformer for either or both of two reasons;
You want to limit or isolate the energy in the control circuit.
You need to change your plant voltage to your chosen control voltage.
The unbalance to the system from a starter coil is negligible.
On the subject of balanced loads:
If you have a 120/208 volt star system you balance your load on the panel by moving loads from one phase to another phase.
If you are using a 240/120:240 volt 4 wire or center tapped delta system it depends.
Four wire delta systems often run unbalanced. They are often a mix of single phase loads and three phase loads. The transformers may be sized accordingly. If you don't know what you are doing, DON"T DO IT.
respectfully
 