jscaufi
Electrical
- Sep 8, 2003
- 13
I have an industrial customer that suffered damage to a 200 hp Baldor 18H Vector Drive. A worker disconnected power to the system, and then about a minute later the plant tripped off. Our substation recloser control saw an OCR (breaker) alarm for min trip level of the OCR, but it didn't trip. This occurred twice, and interviews with the workers revealed the plant tripped twice. Other than that, it was a very quiet day for the utility, with only 2 entries in the log for the entire state we serve (trouble calls in other words).
When power was reset to the plant (I believe a ground fault relay tripped the main breaker), and the tech reapplied power to the drive that had no load on it, just idling, it arced inside, then the upstream breaker smoked. They are unsure if these occurred simultaneously, or one smoked before the other.
Opening the case of the drive revealed severe arcing and pitting of the L1 bus bar at a corner of the metal chassis were it comes within 1/2" of the metal bus bar. The metal bus bar suffered the most arcing to the point it is pitted about 1/8" deep. There are also other signs of arcing throughout the chassis and components. The upstream breaker was a refurbished breaker. It has smoke marks coming out the side seams.
The drive guys says this has never happened with any of their thousands of drives of this model. I compared with an identical drive adjacent to this one and the clearance is a little wider at the point the bad one arced. However, air insulation flashover distances at that voltage are about 0.07 inches. Should be plenty of clearance. Area was a little dusty but not significant.
They brought us in to monitor for a while, which I have commenced. Nothing severe in first 24 hrs. Nothing appeared to get across those contact points, no dead insects, animals, or foreign material on bottom of the case.
I don't see how utility power could do this type of specific damage so limited to one customer, and limited to one breaker and VFD. Previous monitoring for other problems revealed nothing unusual. There are input and output line reactors on each of the two 200 hp drives. Similar problems have intermittently affected these two drives over the past 3 years but nothing this severe. Always seems to happen on weekends, and the problems alternate between drives. A few days prior, we had severe windstorms but it was 11 mph the morning this happened.
Any ideas or suggestions?
thanks
jack
When power was reset to the plant (I believe a ground fault relay tripped the main breaker), and the tech reapplied power to the drive that had no load on it, just idling, it arced inside, then the upstream breaker smoked. They are unsure if these occurred simultaneously, or one smoked before the other.
Opening the case of the drive revealed severe arcing and pitting of the L1 bus bar at a corner of the metal chassis were it comes within 1/2" of the metal bus bar. The metal bus bar suffered the most arcing to the point it is pitted about 1/8" deep. There are also other signs of arcing throughout the chassis and components. The upstream breaker was a refurbished breaker. It has smoke marks coming out the side seams.
The drive guys says this has never happened with any of their thousands of drives of this model. I compared with an identical drive adjacent to this one and the clearance is a little wider at the point the bad one arced. However, air insulation flashover distances at that voltage are about 0.07 inches. Should be plenty of clearance. Area was a little dusty but not significant.
They brought us in to monitor for a while, which I have commenced. Nothing severe in first 24 hrs. Nothing appeared to get across those contact points, no dead insects, animals, or foreign material on bottom of the case.
I don't see how utility power could do this type of specific damage so limited to one customer, and limited to one breaker and VFD. Previous monitoring for other problems revealed nothing unusual. There are input and output line reactors on each of the two 200 hp drives. Similar problems have intermittently affected these two drives over the past 3 years but nothing this severe. Always seems to happen on weekends, and the problems alternate between drives. A few days prior, we had severe windstorms but it was 11 mph the morning this happened.
Any ideas or suggestions?
thanks
jack