naminorite
Electrical
- Aug 20, 2009
- 15
I'm stumped. A EE specified a bank of three, single phase transformers factory wired 120/240V on the secondary side, but required the contractor to wire it into a 208Y/120V. When I approached the EE, he said that the 208Y/120V can be achieved by tying the neutral terminals and leg terminals together. I presumed he meant one of the legs of each single-phase transformer. As I sat and sketched it out, I find that I'm shorting half of my secondary windings and that when I looked at the turns ratio, ended up with a 480V(L-L). I don't believe my L-N voltage would be the 277V, but that is besides the point. Am I missing something here? Can the specified bank of single phase transformers be wired into a 208Y/120V system?