I am analyzing a rectangular mat foundation using plate elements supported by springs.
Only the Soil Bearing Capacity is given in the geotechnical report, thus, I am using a subgrade modulus derived on the SBC value times FS (3) all over the allowable settlement (25mm).
After the analysis, I've noticed that the maximum base pressure of my foundation exceeds the allowable soil bearing capacity. (Say, a max pressure of 200kPa > [SBC = 100kPa], thus Fail)
However, one of our senior structural engineers argued that the footing should still be adequate so long as the maximum displacement is less than the allowable settlement of 25mm.
True enough, maximum settlement is at 16.67mm, which is less than 25mm limit. This doesn't make any sense at all...
Since I essentially removed the factor of safety of 3 when I multiplied the SBC to come up with the subgrade modulus (FS*SBC/25mm),
1) Should the maximum pressure be compared with the soil bearing capacity times the factor of safety? or
2) Should the maximum settlement be compared with the allowable settlement divided by the factor of safety? (25mm/3 = 8.33mm)
Only the Soil Bearing Capacity is given in the geotechnical report, thus, I am using a subgrade modulus derived on the SBC value times FS (3) all over the allowable settlement (25mm).
After the analysis, I've noticed that the maximum base pressure of my foundation exceeds the allowable soil bearing capacity. (Say, a max pressure of 200kPa > [SBC = 100kPa], thus Fail)
However, one of our senior structural engineers argued that the footing should still be adequate so long as the maximum displacement is less than the allowable settlement of 25mm.
True enough, maximum settlement is at 16.67mm, which is less than 25mm limit. This doesn't make any sense at all...
Since I essentially removed the factor of safety of 3 when I multiplied the SBC to come up with the subgrade modulus (FS*SBC/25mm),
1) Should the maximum pressure be compared with the soil bearing capacity times the factor of safety? or
2) Should the maximum settlement be compared with the allowable settlement divided by the factor of safety? (25mm/3 = 8.33mm)