I'm designing a grade beam under a basement retaining wall which I'm modeling as fixed (grade beam / bottom) and pinned (top / floor joist). I checked the foundation retaining wall and it can span between supports with no shear reinforcement required, carrying the full bending moment, and has a deflection of 0.00 inches. About what I would expect for a 7ft tall x 8 in thick conc wall.
So I designed my grade beam for the torsion applied by the fixed bending moment at the bottom and the shear. Ended up with a 18" wide x 24" deep grade beam, (2) #5 bars top, mid and bot, and #4 stirrups @ 6" o.c.
My question is whether I should also require the grade beam to carry the bending moment? This would increase the top and bottom reinforcement to (3) #6 bars top & bot to hit the minimum flexural reinforcement ratio.
And to be fair I haven't got to the drilled shaft design so all this may be revised but the concept for modeling still applies.
I guess the retaining wall doesn't meet the specifications for beam flexural reinforcement ratio with #5 long bars @ 18" o.c. (temp / shrinkage) So I would have to increase the reinforcement in the foundation retaining wall to meet the flexural reinforcement ratio for a beam... which would require more reinforcement than the (3) #6 bars in the grade beam. And also be slightly confusing to specify on the plans. And probably not in line with engineering standards of practice.
I may have just answered my own question.
Image of the detail: [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1681160454/tips/Foundation_Rtg_wall_and_Torsion_Grade_Beam_gxsdr3.pdf[/url]
Thanks
So I designed my grade beam for the torsion applied by the fixed bending moment at the bottom and the shear. Ended up with a 18" wide x 24" deep grade beam, (2) #5 bars top, mid and bot, and #4 stirrups @ 6" o.c.
My question is whether I should also require the grade beam to carry the bending moment? This would increase the top and bottom reinforcement to (3) #6 bars top & bot to hit the minimum flexural reinforcement ratio.
And to be fair I haven't got to the drilled shaft design so all this may be revised but the concept for modeling still applies.
I guess the retaining wall doesn't meet the specifications for beam flexural reinforcement ratio with #5 long bars @ 18" o.c. (temp / shrinkage) So I would have to increase the reinforcement in the foundation retaining wall to meet the flexural reinforcement ratio for a beam... which would require more reinforcement than the (3) #6 bars in the grade beam. And also be slightly confusing to specify on the plans. And probably not in line with engineering standards of practice.
I may have just answered my own question.
Image of the detail: [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1681160454/tips/Foundation_Rtg_wall_and_Torsion_Grade_Beam_gxsdr3.pdf[/url]
Thanks