jimbojr
Civil/Environmental
- Nov 19, 2006
- 1
Working on building renovation and I'm looking at drawing from 1944. The beam designation on the plans is 'B12 16.5', which to me indicates a 12' beam at 16.5 plf. However, when I look at steel manuals on-line, both before and during that time period, the beams designate with B12 are 8" deep beams....makes no sense right?
A site visit revealed the beams are 12" deep with 4' wide flange, and are shaped like WF beams. I do need to confirm the beam capacity.
Can someone provide clarification on the beam designation and/or properties? Is it safe to assume it is FY 36ksi steel and use the dimensions to calculate the allowable stresses?