I am accustomed to using a delta-wye for distribution transformers. But I have recently encountered a grounded wye to grounded wye connection. I've been told that this is a very common connection (but not common to me). I understand the reason for the connection is for ferro resonance, or the avoidance of it. IEEE C57.105 says that this transformer connection is prone to tank heating for unbalanced loads, and that the 3rd harmonic multiples are not suppressed. I have many non-linear loads (numerous VFDs and a large UPS system) on this transformer. All of the system modeling was done using an assumed delta primary.
Are there any known issues with this connection in conjunction with non-linear loads? Am I likely to get nuisance tripping on ground currents? Any advice would be helpful.