Best Choice For Tall Stud Walls

Status
Not open for further replies.

KootK

Structural
Oct 16, 2001
18,573
I've got some 14' 2x6 exterior stud walls. My designer swears to me that they work as 2x6 stud grade @ 8" o/c. Assuming that to be true, and I'll check, is there a practical limit on stud height irrespective of capacity? Should we be using an engineered wood product simply because a straight 2x6 stud grade stud will be difficult to find etc?

Capacity aside, how tall is too tall for regular stud grade stud walls?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Replies continue below

Recommended for you

I find at around 15ft the deflection on a 2x6 stud due to wind becomes problematic.
 
At 15 ft. it is about L/280 with the 30% serviceability reduction and 18 psf load.
We are allowed L/120, but I usually won't go below L/240. If it has brick, I usually won't go below L/360.
 
Yep, you are allowed L/120 and the drywall inside will can crack long before that.
 
Note that you can reduce components and cladding wind loads by 0.7 for calculating deflection. It's buried in a footnote in the IBC somewhere. There are a lot of little tricks in exterior stud design.

When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.

-R. Buckminster Fuller
 
If it has brick, I limit my deflection to H/400 at 50 yr MRI or H/282 for 10 yr MRI. Note that 400*0.7 is about 282, which means the 0.7*wind load for deflection is reducing the MRI. For higher wind zones (hurricane regions) the component and cladding wind load should be multiplied by about 0.55 which gives about H/219. The details of this can be found in an AISC 1993 Journal article by Lawrence Griffis. For other types of cladding, I follow the deflection limits presented in his article and convert to 10 yr MRI.
 
@Dcarr. I don't use L/120 unless I have to try to make something existing squeak by. I have never seen drywall crack in any instance that I could relate to out-of-plane wall deflection.
You would not believe how many houses around here have 18 ft. tall great room walls that are framed out of 2x4's with a double horizontal plate at 9 ft.running about 20 ft. They can be easily shaken by hand but no drywall cracks exist.
 