quizzical1

Mechanical
Jul 6, 2004
180
Hi All,

Can anyone recommend a plastic or range of plastics for use as a potable water commercial plumbing valve body / internals that can accept the stress of NPT connections and water pressures up to 200F @ 150 psig?

We were considering PVC, CPVC, PE, PEX, PE-RT, PP, SP, ABS, and 30% Glass-filled Noryl but was hoping you guys could be able to help us hone in on one - or a better one not listed - which could be injection molded easily.

TIA,

~Q

 
Replies continue below

Recommended for you

Diameter matters.


However, I don't think you're going to find any plastic that will work reliably at those temperatures and pressures while also using NPT threads. The tapered threads have a wedging effect that elevates the stress into the the creep region. Glass reinforcement will help. If you're working with dissimilar materials, high coefficient of thermal expansion of plastic is also a challenge for NPT connections.
 
Other questions are why such a high temp and pressure for a domestic hot water system? Hospitals don't even take them that high when disinfecting.
 
Sorry guys, some clarification:

Tug - largest size would be 1" NPT (thanks for the link)

Pedarrin2 - nominal temp ~140F and 180F for disinfection. Or the use of chemical (Chlorine Dioxide)

Working pressures would typically be 50 - 80 psig but am concerned about structural integrity (hence the glass filled option)of the valve assembly in a pipe run.
 