Best Practices When Detailing a Non-Load Bearing CFS Wall Sitting On a Roof Edge

Status
Not open for further replies.

MJC6125

Structural
Apr 9, 2017
120
See image below for two similar conditions. They are both for a CFS non-load bearing wall sitting on the edge of a low roof at a roof step. One is when we have steel joists bearing on the edge beam, and one is where the edge beam is parallel to the joists. I have a few questions related to these details.

Wall_at_roof_edge_eiazlg.jpg


1. For case 1, do you automatically need to have an edge angle of some sort to fasten the edge of your diaphragm to? I think the answer is yes or some sort of blocking pieces between each joist.

2. For case 2, would you use an edge angle like shown or is that unnecessary because the steel beam is what the deck is fastened to and the beam can act as your diaphragm chord/collector?

3. Assuming this is a non-load bearing wall with no brick veneer, are you OK with setting the studs directly on the metal deck or do you stop the metal deck to the right of the wall and sit the wall directly on structural steel?

4. Does the vertical leg of the edge angle create an access issue for screwing the bottom track to the studs at the base of the CFS wall? Is that an issue that needs to be remedied or would the contractor build the wall on the ground first and then set it in place and fasten down the bottom track?


I know roof flashing and architectural considerations may play into these details, but I wanted to see if anybody had preferences on what they do structurally.
 
Replies continue below

Recommended for you

1. Yes, though it doesn't have to be an angle. 2.5" tubes between joists may be the better option as it precludes joist rollover by transferring the diaphragm shear directly to the collector. For lightly loaded diaphragms you can check rollover to see if it's an issue.

2. No. Beam is the collector as you mentioned.

3. Yes, sit it on the deck. If this is going to be 30 feet high, I might reconsider, but a roof step or even an 8ft wall (if non-bearing) would likely be light enough to not matter. If it does matter, then stuff some fire treated blocking in under the flutes of the deck. SDI's manuals are good for checking point loads, etc. on deck.

4. It would. Another reason to just leave it off.
 