All,
We have a 4160V, ~3MW diesel genset that went through some bad juju with arcing in the entrance cubicle of its attached switchgear cubicle. Previous loss of PT fuses on shutdown led the voltage regulator to take it very high on ramp up from idle to rated (perhaps as high as 150% and for a second or two prior to fault?). Excitation was cut immediately by protection relaying on fault but the decay may have taken 2sec. Surge arresters in the entrance cubicle were blown out so not sure what voltage spikes the alternator may have seen during this event.
Most of our installed base is in low voltage territory and we have not had problems with our newer 4160 equipment. Initially, the electricians meggered it at 1000VDC (looked good including polarization index). The OEM manual for it says to megger at only 500VDC?! I thought that a bit odd for a 4160V machine. Does a megger at 500VDC tell one much about insulation on a 4160V machine? Given the above scenario, does megger testing seem sufficient?
Also, trying to get up to speed on what testing, if any, might be suggested beyond this. Ramped vs Stepped DC Voltage Testing? This sounds preferable to AC or DC Hi-potting, even if either of these two are at some acceptable range less than what new test standards would say (but at least equal or higher than the machine rated voltage)?
I did find these two posts helpful and had already planned to investigate IEEE 95:
thread237-147223
thread237-301242
Any additional guidance or reference to links or other testing standards would be highly appreciated. We do have a spare alternator and can handle the associated downtime if necessary to replace it now. It would be much more painful for us to find out 6 months down the road that something was wrong and then have to replace it.
Thanks for any and all help!
We have a 4160V, ~3MW diesel genset that went through some bad juju with arcing in the entrance cubicle of its attached switchgear cubicle. Previous loss of PT fuses on shutdown led the voltage regulator to take it very high on ramp up from idle to rated (perhaps as high as 150% and for a second or two prior to fault?). Excitation was cut immediately by protection relaying on fault but the decay may have taken 2sec. Surge arresters in the entrance cubicle were blown out so not sure what voltage spikes the alternator may have seen during this event.
Most of our installed base is in low voltage territory and we have not had problems with our newer 4160 equipment. Initially, the electricians meggered it at 1000VDC (looked good including polarization index). The OEM manual for it says to megger at only 500VDC?! I thought that a bit odd for a 4160V machine. Does a megger at 500VDC tell one much about insulation on a 4160V machine? Given the above scenario, does megger testing seem sufficient?
Also, trying to get up to speed on what testing, if any, might be suggested beyond this. Ramped vs Stepped DC Voltage Testing? This sounds preferable to AC or DC Hi-potting, even if either of these two are at some acceptable range less than what new test standards would say (but at least equal or higher than the machine rated voltage)?
I did find these two posts helpful and had already planned to investigate IEEE 95:
thread237-147223
thread237-301242
Any additional guidance or reference to links or other testing standards would be highly appreciated. We do have a spare alternator and can handle the associated downtime if necessary to replace it now. It would be much more painful for us to find out 6 months down the road that something was wrong and then have to replace it.
Thanks for any and all help!