Bias slope of Generator differential relay

Status
Not open for further replies.

tsknan

Electrical
Jan 30, 2009
16
In Micom P341 relay can any body explain exactly what does the meaning of slope k2(manufacturer reccoments 150% for this setting),normaly we use slope of 0.25 or some thing like that for a differential relay,but here the value is some what confusing,please clarify,how we can draw the chjaracteristics
settings: Is1=60ma,Is2=1A,K1=0,K2=150%,CTR 2500/1 for both side CTs used in generator protection of 23MVA hydro Generator,1A nominal current
 
Replies continue below

Recommended for you

K2 is a second slope, it is meant to add stability should a CT start to saturate.

The second slope is active when the bias current is above the Is2 setting.

25% is a typical slope 1 (K1) setting for a transformer differential relay to account for spill current introduced by the tap changer (mainly).
 