DouginMB
Mechanical
- Dec 16, 2002
- 87
I am having problems with a VAV terminal box serving a row of offices along the exterior of an office building. The VAV box discharges 83F air. The duct discharges from the box into about a 5 foot run of rectangular duct and into a dovetail wye fitting. The duct then runs each way over the office spaces. A 6 ft. length of round branch duct taps off each duct to a ceiing square cone diffuser for each office. The air discharging from the diffuser is 5 degrees lower than the discharge are from the VAV box. The temperature off the air at the entrance to the wye fitting averaged 81F. The duct is wrapped with 2" blanket insulation and vapor barrier. Branch ducts are insulated as well. The insulation is well sealed. I'm measuring the 5 degree drop out of a diffuser that is only 15 linear feet away from the VAV. The diffusers down the at the end of the duct trunk are discharging 76 degree air. Also, I've had the airflow measured at the diffusers and they match the minimum design settings. I'm absolutely baffled and would appreciate any insight or ideas as to what might be happening.