Blast wall requirement between substation transformers

Status
Not open for further replies.

tinfoil

Electrical
Jun 24, 2004
351
Is anyone aware of any actual standard(s) that cover the requirement, if any, of installing blast walls between two or more substation transformers? I'm looking for specs re. minimum distances before they are required and/or recommended. If they are required, what sort of force/overpressure must they withstand?

My specific application is two 21/28/35MVA 115000:12470 transformers installed 49' (on center) apart in a legacy substation. There is no blast wall at present. We are replacing one (since it dates back to 1930!), and someone wants to install a masonry blast wall between them as part of the project. Unfortunately, that would also block an access road within the substation.
 
Replies continue below

Recommended for you

I don't think they're required unless it's by your insurance company. FM Global has recommendations. Also see NFPA 850.

Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.
 
Check the following:

- IEEE Std 979, “IEEE Guide for Substation Fire Protection,”

- IEEE Std C2, "National Electrical Safety Code (NESC)

- NFPA 850-1992, “Recommended Practice for Fire Protection for Electric Generating Plants”

- Code of Federal Regulations, Part 112 “Oil Pollution Prevention” (40CFR112)
 