Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Blowdown pipe erosion

Status
Not open for further replies.

bepalo

Civil/Environmental
May 16, 2011
3
Have a surface blowndown line 1" in dia. It tees into a 2" forged steel tee. Boiler pressure is about 100 psi. The eroded spot is directly above the tee and the reducer from 1" to 2" is about 6" prior to the tee. Downstream it leads to a drain. The failure occurred after approximately 18 months. I'm suspecting mechanical erosion, does anyone else have any thoughts on the failure?
IMG_1970_qvg6jn.jpg
 
Replies continue below

Recommended for you

Yes this can be typical for carbon steel blowdown lines. You need a more direct path for blow down versus a Tee.
 
You also need an alloy with higher Cr, maybe 2.5%.
Combine this with improved flow path and you will never repair this again.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube
 
Nothing unusual about metal erosion in blowdown connections. A certified welder whose firm has a valid NB Repair stamp will have to go inside the steam drum to repair.
 
Could this location be a low point in the flowpath where condensate could have collected ? Vapor blowdown lines should always be free draining, including any dead ends.
 
Ed Stainless is spot-on ....

For several fossil projects, I have seen blowdown piping configured with a sacrificial erosion "target".

Schedule 80 Low alloy material (A335-P22)was commonly used.

316 Stainless steel piping can also be used....

MJCronin
Sr. Process Engineer
 
Just replace the reconfigured blow down piping with Grade P22 or even a Grade P5 material.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor