Ah, the semantics issues rears it's ugly head.
The A-B Bul. 140 is not a "circuit breaker" by North American definition, it is what is called a "Motor Protection Switch", a.k.a. "Manual Motor Starter", a.k.a. "Motor Starter Protector" etc. etc., but we generally don't use the term "circuit breaker" here because that implies a specific set of design criteria (reserved for MCCBs) that those devices do not possess, chiefly UL489 listing or recognition.
These devices include the OL protection as an adjustable dial, the same as on bi-metal IEC overload relays. It also possesses a fixed Instantaneous Magnetic Trip function and a disconnecting means. So one of these devices + a contactor constitutes a complete "Type E Combination Starter" listed under UL508.
These are not particularly robust devices compared to older traditional Combination Motor Starters that use an MCCB as the protection device. A short circuit, even if the device interrupts it successfully, is likely to damage it. They are essentially a "one shot" protective device; the official term is "self protected", meaning they will sacrifice themselves in the line of duty, but don't expect them to be reusable (something expected of an MCCB).
So it's entirely possible that you have something in the circuit that is giving you an intermittent dead short to ground or a bolted fault, and that little device is "throwing itself on the grenade" to prevent a fire.