Can someone explain what I encountered?
I was troubleshooting a 3Ø 480VAC motor. When I put my meter on each fuse, leg to ground the reading was ~280VAC, on any leg, top or bottom of the fuse. Which made me believe the fuse was good. But if I were to check phase to phase, at the bottom of the fuse, it was only 5 or 6 volts, leg to leg. Changing the fuses did resolve the issue, just left me confused.
The fuses were Buss, Low-Peak, Dual Element Time Delay LPJ-5SP Current Limiting.
Thanks in advance.
I was troubleshooting a 3Ø 480VAC motor. When I put my meter on each fuse, leg to ground the reading was ~280VAC, on any leg, top or bottom of the fuse. Which made me believe the fuse was good. But if I were to check phase to phase, at the bottom of the fuse, it was only 5 or 6 volts, leg to leg. Changing the fuses did resolve the issue, just left me confused.
The fuses were Buss, Low-Peak, Dual Element Time Delay LPJ-5SP Current Limiting.
Thanks in advance.