Hello all,
I am looking at some PSV discharge piping calculations using Hysys for choked vapour flow. One thing that I am finding is that it appears that there is choking in the outlet nozzle of the valve. Having read around this is I see it is called body bowl choking but is more of a concern for large relief valves with high set pressures. The relief valves I am looking at have set pressures of around 20 barg at F and G sizes.
For example I have a 1.5F2 conventional relief valve with a set pressure of 20 barg relieving steam. If I model it with a 2"x3" reducer located directly on the PSV outlet nozzle then all is well and velocities/backpressure requirements are easily met with a short discharge line to atmosphere. However, if I put in a very short length of 2" pipe to represent the outlet nozzle of the PSV then it shows that the flow chokes in this 2" section. The only way I can see to remove this choke is to increase the downstream pressure (by adding some sort of restriction downstream), which increases the pressure/density at the 2" section. I feel I am probably missing something here... is this a concern? Would it be reasonable to ignore the valve outlet flange? I suppose ulitimately if I check that there is no choke at a back pressure of 10% of set pressure then it should be ok. It seems to be a problem with lots of my relief valves in hydrocarbon service and they are only F and G sizes.
I am looking at some PSV discharge piping calculations using Hysys for choked vapour flow. One thing that I am finding is that it appears that there is choking in the outlet nozzle of the valve. Having read around this is I see it is called body bowl choking but is more of a concern for large relief valves with high set pressures. The relief valves I am looking at have set pressures of around 20 barg at F and G sizes.
For example I have a 1.5F2 conventional relief valve with a set pressure of 20 barg relieving steam. If I model it with a 2"x3" reducer located directly on the PSV outlet nozzle then all is well and velocities/backpressure requirements are easily met with a short discharge line to atmosphere. However, if I put in a very short length of 2" pipe to represent the outlet nozzle of the PSV then it shows that the flow chokes in this 2" section. The only way I can see to remove this choke is to increase the downstream pressure (by adding some sort of restriction downstream), which increases the pressure/density at the 2" section. I feel I am probably missing something here... is this a concern? Would it be reasonable to ignore the valve outlet flange? I suppose ulitimately if I check that there is no choke at a back pressure of 10% of set pressure then it should be ok. It seems to be a problem with lots of my relief valves in hydrocarbon service and they are only F and G sizes.