Boiler fan trip
SA07
MU
Good morning
Our power plant stopped following the trip of a boiler fan due to a disturbance on the utility grid.
The fan is controlled by a simocode, soft starter & bypass contactor.
In the past several times, our power plant has islanded following disturbance/fault on the utility grid.
After the trip, we have restarted the plant and everything is working well up to now. We have not replaced any equipment.
1) Can you plz check if our simocode settings are correct?
2) Is the wiring correct?
3) Is the setting of under voltage in the simocode correct?
4) What may be the cause of the trip?
5) Can we disable the under voltage setting in the simocode?
6) Can the last alarm in the simocode alarm list be the cause of the trip? (Trip level U<)
After the boiler fan has tripped, then boiler tripped, then turbine tripped and our line breaker also has opened. So our plant was in a black out.
Plz see attached word doc with all details.
 https://files.engineering.com/getfile.aspx?folder=b4099eef-a85f-40bd-a6ac-3cd0c2aab3c2&file=Trip_Boiler_fan.docx
Power plant control voltage was transferred to industrial UPS with redundancy and automatic transfer switch. It happened that one UPS became faulty in the past and all supply was switched to the redundant UPS without stopping the power plant.