I have a customer who experianced the following which is something he does not want to repeat. Does anyone have an idea what caused this?
The Pump is a 3GT I-R Boiler Feed Pump, Steam Turbine Driven, 240-257 deg F water from DA tank
Pump was shut down and not turning but hot or at least warm
Discharge valve downstream of pump was closed first. This valve was some distance away from pump (20-30’?)
Pump has discharge check valve
Bypass Line to DA Tank from Pump discharge was open
Suction Isolation Valve (Gate valve) was manually closed – takes maybe 30 seconds
There is an expansion joint on suction side next to the pump
A loud explosion/noise was heard by the person closing the suction valve immediately when the suction line valve was closed and there was violent movement of the suction line to such an extent that the hold down anchors for the suction line pipe support (next to the pump) were ripped from the floor. The expansion joint was extended to its maximum.
Operator was visibly shaken and doesn’t want to go through this again
If you have any ideas please let me know. I have asked the customer to check on a couple of theories I have but I want tell you what they are as I don’t want to color your thinking.
The Pump is a 3GT I-R Boiler Feed Pump, Steam Turbine Driven, 240-257 deg F water from DA tank
Pump was shut down and not turning but hot or at least warm
Discharge valve downstream of pump was closed first. This valve was some distance away from pump (20-30’?)
Pump has discharge check valve
Bypass Line to DA Tank from Pump discharge was open
Suction Isolation Valve (Gate valve) was manually closed – takes maybe 30 seconds
There is an expansion joint on suction side next to the pump
A loud explosion/noise was heard by the person closing the suction valve immediately when the suction line valve was closed and there was violent movement of the suction line to such an extent that the hold down anchors for the suction line pipe support (next to the pump) were ripped from the floor. The expansion joint was extended to its maximum.
Operator was visibly shaken and doesn’t want to go through this again
If you have any ideas please let me know. I have asked the customer to check on a couple of theories I have but I want tell you what they are as I don’t want to color your thinking.