Boiler Room heat control
carlosgw
167
Direct vent boilers eliminate the need for boiler room air vents for combustion air and dilution air. The boiler rooms (or central domestic hot water rooms) still get hot (esp. since they are getting smaller). Is there any criteria for heat to the boiler room that can be used to design a heat control ventilation system?
Many boilers list a heat loss (radiation). You've also got insulated pipe and pumps. Amount of loss depends on boiler, insulation level, size of room, etc.
However, I'd say that a heat gain of 1% of boiler load would be a reasonable assumption for a heat control vent system.
One good thing of having it already in place is that you can measure actual higest temperature reached.
When you put it in equation for heat rejection together with desired max. room temperture and coincidental outside temperature, you will get exhaust air flow needed.
You will have, however, to recheck and eventually redesign system of introducting fresh air for combustion purposes.