Hi All,
I am currently designing a structural steel beam supports for an existing slab, Actually there is an existing roof slab resting on walls of tank approx. dimension of slab are(25.7m x 5.8m x 0.25m thick) and now client wants to saw-cut a 2000 x 1000 m opening in the slab and need us to design steel beam support below the opening to resist any stresses induced.
I have attached the drawing of steel work proposed for reference
Now the Primary beams are subjected to UDL of 14 kN/m due to slab SW and Live load and two concentrated point load of magnitude 3.2 kN due from secondary beam connection.
the Max. Bending mmt at center of the span is 62.6 kN.m, Max. Shear at support is 43 kN and Max deflection 9.08 mm which is under control.
Section used for Primary beam (UB 356 x 171 x 45)
Now the actual problem is due to some site constraints the contractor and client requires a splice connection to half the beam span length and they are asking for splicing the bottom flange and web only. So is it possible to splice a beam at center that too only on bottom flange and web? Or is there any other solution for this case?
P.S. - Beams are needed to splice because of lifting into place constraints.
(Design is as per BS EN 1992-1-8)
(Beams are simply supported on both sides)
I am currently designing a structural steel beam supports for an existing slab, Actually there is an existing roof slab resting on walls of tank approx. dimension of slab are(25.7m x 5.8m x 0.25m thick) and now client wants to saw-cut a 2000 x 1000 m opening in the slab and need us to design steel beam support below the opening to resist any stresses induced.
I have attached the drawing of steel work proposed for reference
Now the Primary beams are subjected to UDL of 14 kN/m due to slab SW and Live load and two concentrated point load of magnitude 3.2 kN due from secondary beam connection.
the Max. Bending mmt at center of the span is 62.6 kN.m, Max. Shear at support is 43 kN and Max deflection 9.08 mm which is under control.
Section used for Primary beam (UB 356 x 171 x 45)
Now the actual problem is due to some site constraints the contractor and client requires a splice connection to half the beam span length and they are asking for splicing the bottom flange and web only. So is it possible to splice a beam at center that too only on bottom flange and web? Or is there any other solution for this case?
P.S. - Beams are needed to splice because of lifting into place constraints.
(Design is as per BS EN 1992-1-8)
(Beams are simply supported on both sides)