Hi all,
I am looking for some guidance on the bonding of Steel Welding benchs for a training facility with 10 such benches. The benches were previously bonded using a 2.5mm PE back to the main earth node. A trainee then subsequently went arc welding without attaching the welder earth clamp directly to the table but must have connected it to some other steel structural column which was bonded. This resulted in the return path for the welder current running through a section of the 2.5mm PE and destroying it.
I cannot find anything specific regarding european regulations regarding bonding of welding benches as as such I am unsure whether it is neccessary or not. If it is neccessary then is the use of Earth Continuity Monitors or alternatives required to protect the PE?
Any help appreciated.
I am looking for some guidance on the bonding of Steel Welding benchs for a training facility with 10 such benches. The benches were previously bonded using a 2.5mm PE back to the main earth node. A trainee then subsequently went arc welding without attaching the welder earth clamp directly to the table but must have connected it to some other steel structural column which was bonded. This resulted in the return path for the welder current running through a section of the 2.5mm PE and destroying it.
I cannot find anything specific regarding european regulations regarding bonding of welding benches as as such I am unsure whether it is neccessary or not. If it is neccessary then is the use of Earth Continuity Monitors or alternatives required to protect the PE?